HTP Versa-Hydro F00 — Water High Temperature
F00
Water high temperature. The water in the tank has overheated (red fault light, LOCKOUT flashing; pump runs to cool the appliance). Check central heating pump operation and that water is moving through the system with all ball/zone valves open or closed as intended; observe the temperature/pressure gauge - if the water is not hot check the wiring to the water ECO sensor and repair if necessary; if the wiring is intact, water is not excessively hot and the code persists, replace the ECO sensor. The table classifies it as Lockout (Manual Reset).
Applies to
This overheating code is displayed by the 926 SIT control on Versa-Hydro models (PHE130/PHE199), as documented in Versa-Hydro Installation Manual, LP-314 Rev. 012 Rel. 007 (12.8.21), Table 21 (LP-314). Codes can differ between controller generations, so always check the manual that matches your unit.
- HTP Versa-Hydro & Versa-Hydro-Solar (discontinued)
- HTP PHE130-55
- HTP PHE130-80
- HTP PHE130-119
- HTP PHE199-55
- HTP PHE199-80
- HTP PHE199-119
- HTP PHE130-80S
- HTP PHE130-119S
- HTP PHE199-80S
- HTP PHE199-119S
Controller: 926 SIT control. Source manual: LP-314.
Why a code is not a diagnosis
An over-temperature code protects the heat exchanger or venting; it does not reveal whether the cause is low water flow, a failed pump, trapped air, fouling or a sensor fault.
Safe things to observe
- Note the code and whether rooms or hot water are still working.
- If you see steam, melted wiring or smell burning, switch the appliance off at its service switch and call a technician.
Do not
- Do not reset the appliance repeatedly while the cause is unknown.
- Do not remove covers or bypass any high-limit device.
How professional service helps
- A technician checks pump operation, flow, system pressure and the cleanliness of the heat exchanger.
- Combustion and safety devices are verified with an analyser and the manufacturer's procedure after any repair.
Where ROMA provides on-site service
On-site service is currently offered in Greater Vancouver, BC, including Vancouver, Burnaby, Richmond, Surrey, Coquitlam, North Vancouver, West Vancouver, New Westminster, Port Coquitlam, Port Moody, Delta, Langley, Maple Ridge, Abbotsford, Chilliwack, White Rock, Pitt Meadows, Tsawwassen, Anmore, Lions Bay, Belcarra, Bowen Island, Mission. Everything else on this site is reference information you can use anywhere in Canada.
Parts and service
Parts commonly involved
These parts appear in the documented text for this alert. A code reports a condition, not a failed part — a technician confirms the cause by testing before anything is replaced.
Boiler sensors (thermistors)
Boiler sensors are small temperature probes, usually thermistors, that tell the control how hot the water and flue gases are so it can fire safely…
What a technician checks →Zone valve
A zone valve lets one boiler heat several areas at different temperatures by opening or closing the water flow to each zone on demand.
What a technician checks →Circulator pump
The circulator is the pump that moves heated water from a boiler out to the radiators, baseboards or in-floor loops and back again.
What a technician checks →Pressure gauge
The pressure gauge is the boiler's dashboard: it shows the water pressure in the system, and often the temperature too.
What a technician checks →
Service for this alert
- Gas Boiler Repair
Licensed gas technicians from ROMA Heating & Cooling diagnose and repair residential and light-commercial gas boilers across…
- Emergency Boiler Repair
Priority gas boiler repair for homes and buildings in Greater Vancouver with no heat, no hot water, a locked-out boiler or a leak.
Every boiler part explained — what it does, how it fails and what a technician checks.
Documented for HTP Versa-Hydro & Versa-Hydro-Solar (discontinued).
Frequently asked questions
Can I clear this code myself?
Clearing a code without fixing its cause usually just brings it back. Note the code, check the safe items on this page, then call a licensed technician. If your appliance manual describes a user reset for this exact code and it stays away, no call may be needed.
Boiler locked out? Call with the alert text ready.
The brand, model and this alert are passed along when you request service online, so the technician arrives prepared.
On-site service in Greater Vancouver, BC. ROMA lists “Open 7 days” on its site; call to confirm same-day availability.
Sources and verification
- Versa-Hydro Installation Manual, LP-314 Rev. 012 Rel. 007 (12.8.21), Table 21 · LP-314 · accessed September 8, 2026
Facts checked September 8, 2026. Last updated September 8, 2026. Technical reviewer: not yet assigned.