Weil-McLain AquaBalance F15 — Minimum and Maximum Frequency Feedback From Fan Error

F15

Needs attentionWeil-McLain AquaBalance Series 2 (A## hard lockouts and F## soft lockouts, manual 550-100-325)

Minimum and maximum frequency feedback from fan error. If the controller measures fan frequency lower than 20Hz or higher than 295Hz, the error is set after 15 seconds and heat demands are disabled. The table classifies it as Soft Lock-out – Automatic Reset.

Applies to

This venting or air-supply fault code is displayed by the AquaBalance control (A##/F## fault codes) on AquaBalance Series 2 models (AB-80, AB-120, AB-155 and combi AB-80C, AB-120C, AB-155C), as documented in AquaBalance Series 2 Boiler Manual, doc 550-100-325/0924 (fault code tables 3 and 4) (550-100-325/0924). Codes can differ between controller generations, so always check the manual that matches your unit.

Controller: AquaBalance control (A##/F## fault codes). Source manual: 550-100-325/0924 (2024-09).

Why a code is not a diagnosis

A venting or air-supply code points at the combustion-air path: a blocked terminal, a restricted flue, a failed fan, or a condensate restriction. It does not say which, and running an appliance with a blocked flue is unsafe.

Safe things to observe

  • If a carbon-monoxide alarm sounds anywhere in the building, leave immediately and call 911 from outside.
  • From a safe distance, check that the vent terminal and combustion-air inlet are not blocked.
  • Do not run the appliance while a blockage is suspected.

Do not

  • Do not put anything into the vent or air-intake openings.
  • Do not remove or modify vent pipe.

How professional service helps

  1. A technician inspects the full vent and combustion-air path, clears blockages and checks the fan.
  2. Combustion and safety devices are verified with an analyser and the manufacturer's procedure after any repair.

Where ROMA provides on-site service

On-site service is currently offered in Greater Vancouver, BC, including Vancouver, Burnaby, Richmond, Surrey, Coquitlam, North Vancouver, West Vancouver, New Westminster, Port Coquitlam, Port Moody, Delta, Langley, Maple Ridge, Abbotsford, Chilliwack, White Rock, Pitt Meadows, Tsawwassen, Anmore, Lions Bay, Belcarra, Bowen Island, Mission. Everything else on this site is reference information you can use anywhere in Canada.

See all service areas

Parts and service

Parts commonly involved

These parts appear in the documented text for this alert. A code reports a condition, not a failed part — a technician confirms the cause by testing before anything is replaced.

Service for this alert

  • Gas Boiler Repair

    Licensed gas technicians from ROMA Heating & Cooling diagnose and repair residential and light-commercial gas boilers across…

Every boiler part explained — what it does, how it fails and what a technician checks.

Documented for Weil-McLain AquaBalance.

Frequently asked questions

Can I clear this code myself?

Clearing a code without fixing its cause usually just brings it back. Note the code, check the safe items on this page, then call a licensed technician. If your appliance manual describes a user reset for this exact code and it stays away, no call may be needed.

Boiler locked out? Call with the alert text ready.

The brand, model and this alert are passed along when you request service online, so the technician arrives prepared.