Skip to content
Boilers.caby ROMA Heating & Cooling

IBC Technologies · Error codes

IBC SFT-1 F006 — Flame detected when burner is off

F006

SafetyIBC Superflow SFT-1 tankless water heater with the numeric-display control

The controller detected a flame signal at a moment when the burner should be off. A stray flame signal can indicate a gas valve passing gas when closed, an electrical fault, or a sensor/grounding problem, so the unit shuts down.

Applies to

This fault is shown by the numeric-display touch panel control on Superflow SFT-1 tankless water heaters (SFT 199-1), as documented in IBC Installation & Operating Instructions — SFT 199-1 tankless water heater, doc 84160406, sections 5.3.1–5.3.3.

Controller: numeric-display touch panel control. Source manual: 84160406 (2024-09).

Why a code is not a diagnosis

The code does not say whether the signal is a real flame (gas valve leaking through) or an electrical artifact from grounding or a faulty module. Both paths are on the manual's check list and both need a technician.

Safe things to observe

  • Treat this code seriously: if gas is passing when it should not, there is a hazard.
  • If you smell gas, leave the building immediately and call FortisBC at 1-800-663-9911 or 911 from outside.
  • Turn the appliance off at its service switch if you can do so safely.

Do not

  • Do not reset or run the appliance after this code without a technician's diagnosis.
  • Do not touch the gas valve.

How professional service helps

  1. A technician verifies grounding and internal/external power supply quality.
  2. The gas valve is tested to confirm it closes at the end of a demand; the ignition module or control module is replaced if the fault points there.

Where ROMA provides on-site service

On-site service is currently offered in Greater Vancouver, BC, including Vancouver, Burnaby, Richmond, Surrey, Coquitlam, North Vancouver, West Vancouver, New Westminster, Port Coquitlam, Port Moody, Delta, Langley, Maple Ridge, Abbotsford, Chilliwack, White Rock, Pitt Meadows, Tsawwassen, Anmore, Lions Bay, Belcarra, Bowen Island, Mission. Everything else on this site is reference information you can use anywhere in Canada.

See all service areas

Parts and service

Parts commonly involved

These parts appear in the documented text for this alert. A code reports a condition, not a failed part — a technician confirms the cause by testing before anything is replaced.

Service for this alert

  • Gas Boiler Repair

    Licensed gas technicians from ROMA Heating & Cooling diagnose and repair residential and light-commercial gas boilers across…

  • Emergency Boiler Repair

    Priority gas boiler repair for homes and buildings in Greater Vancouver with no heat, no hot water, a locked-out boiler or a leak.

Every boiler part explained — what it does, how it fails and what a technician checks.

Documented for IBC Technologies Superflow SFT-1 Tankless.

Frequently asked questions

Is flame-when-off dangerous?

It can be, because one possible cause is a gas valve passing gas while the burner is off. Until a technician confirms otherwise, treat the appliance as needing service before it runs again.

Boiler locked out? Call with the alert text ready.

The brand, model and this alert are passed along when you request service online, so the technician arrives prepared.

On-site service in Greater Vancouver, BC. ROMA lists “Open 7 days” on its site; call to confirm same-day availability.

Sources and verification

Facts checked September 7, 2026. Last updated September 7, 2026. Technical reviewer: not yet assigned.